This main center beam is a w12x14, spanning 30 ft on a 1/12 pitch to center. It has an equally spaced load of approximately 1500 lbs on it from the roof. The plates that join the four members have 3/4" diameter bolts. My question is what would my deflection be with an additional 1000 lbs loaded at the center?
Thanks guys,
Rod
Thu Aug 16, 2012 3:24 pm
Post Re: Structural eng. calc's needed please
That is an MBS drawing. I can mimic it let you know after i load the frame for 1k of force at the peak. Give me a minute. I have a feeling it will fail as per MBS... But i will giv you a delflection.
Bayou Surface Drive
337-351-0362
Tarkington, TX 77327
Thu Aug 16, 2012 3:38 pm
Cool thx
Thu Aug 16, 2012 3:47 pm
assuming you have w12x14 columns and rafters, about 9/16" defelection at the peak.
I ran it with and without the load and the deflection is the same.
Bayou Surface Drive
337-351-0362
Thu Aug 16, 2012 3:48 pm
Ok. It will never have that much on it, but I hear 1/2" is as much deflection that is acceptable.
Thu Aug 16, 2012 3:50 pm
Bayou Surface Drive
337-351-0362
Fri Aug 17, 2012 6:13 am
Glad i found this post, the inner nerd in me is excited about breaking out the AISC manual after work now, just for the hell of it.
Gator Trax 1644 HD pushed by a screamin' MB Mini 35
Fri Aug 17, 2012 6:41 am
Bayou Surface Drive
337-351-0362
Fri Aug 17, 2012 6:59 am
Fri Aug 17, 2012 8:21 am
It is a vertical connection with the connection plate extending beyond the top and bottom flange. It appears to have 8 bolts per connection at the peak and at each haunch connection.
Bayou Surface Drive
337-351-0362
Fri Aug 17, 2012 8:59 am
work got s-l-o-w. here is a rough calculation, assuming A992 steel, and treating the apex bolted connection as a "fixed" connection, and calculating for max deflection at the center (essentially treating the member as one continuous beam). I did not include any wind load nor construction live load. I do not have much experience with this particular type of connection, and now i build roads, but was pretty dang close to your program, maxxis
Fri Aug 17, 2012 12:18 pm
Well when you add wind load and dead load of the roof framing and panels you get a touch more. Note at FULL wind load. Looks like we was close!
Bayou Surface Drive
337-351-0362
Mon Aug 20, 2012 7:20 am
Can y'all stamp those calcs plz so i know who to blame when it falls on me. Lol
Mon Aug 20, 2012 8:13 am
:lol: That type of figure'n always impressed the smack out of me !!!! Good Job fellers !!!!
Mon Aug 20, 2012 8:41 am
Bayou Surface Drive
337-351-0362
Mon Aug 20, 2012 9:12 am
Mon Aug 20, 2012 1:04 pm